If you go that route, NEC requires a four conductor feed on the 240 line (2 hot, a neutral and ground) if separate loads are used on each hot leg (that is why newer model electric clothes dryers have 4-prong plugs on them). The CV Electrical box come pre-configured with a 120 V cord ready to plug into a standard 15-amp outlet for power to the remote unit and contactor coil, so why rewire what you've already paid for. Your cost for the 240 wire will be higher (10/2 versus 10/3 NM cable). In my experience with my Bin Sensor power supplies, having them on a circuit with a motor can cause electronics failures and your proposal may impact the electronics in the remote control outlet pre-configured with the electrical box. The cause of failures is a voltage drop on the 120 leg when the CV blower motor comes on and draws heavily to get the impeller up to speed. That configuration may cause the electrical box remote to fail. I'd recommend you use a separate 120 V outlet with the Electrical Box as designed. If you decided to purchase one of the Bin Sensors from CV (which I supply), I cannot warrant it with the 120 volt power on the motor power leg.