Actually, the National Electric Code may require #8 copper wire, depending on the wiring method. The sizing of motor circuits (Article 430 of the NEC) is different than most other circuits. Here is a quick run down:
The wire to the motor (the branch circuit) is sized according to a current value looked up in a table, not according to the nameplate current value. For a 5 HP 240V motor, that current value is 28 amps. The required ampacity (current carrying ability) of the branch circuit is then 125% of that value, which is 35 amps.
To determine what size wire to use, you need to check an ampacity table based on the wiring method. If you are using Romex (NM Cable, 60 degree column), then the ampacity of #10 Cu is only 30 amps, so you have to use #8 Cu, which has an ampacity of 40 amps. If you are runnning conduit to the motor and pulling individual conductors (eg THHN, 75 degree column), then the ampacity of #10 Cu is 35 amps and #10 Cu is OK.
Lastly, as to breaker size, it is important to understand that for a motor circuit, the breaker does not protect the motor. The motor is protected by the motor overload, which for the Leeson motor sold here is an integral thermal protector on the motor. So the job of the breaker is just to deal with short circuits and ground faults. With that in mind, the NEC allows a normal breaker (an inverse time breaker) to be sized up to 250% of the tabular current value for the motor. In our case, that is 28 amps * 250% = 70 amps.
One of the reasons this is so high is that the motor starting current is much higher than the normal full load current, and if you size the breaker too low, you will get nuisance trips on starting. However, there is nothing wrong with using a smaller breaker if it works without nuisance trips. Since people here have reported using a 30 amp breaker without problems, I would start with that and only upsize if necessary.
Hope that helps. It is surprising to note that wiring the motor used here with #10 Romex is an NEC violation.
Cheers, Wayne