The assembly manual calls for clockwise rotation wiring on page 22:
.
[FONT="][/FONT]
[FONT="] [/FONT]
[FONT="] "Once the motor is wired, the motor shaft and [/FONT]
[FONT="] impeller blade should be turning counter-clockwise [/FONT]
[FONT="] when viewing from below. (ie: looking up at the motor [/FONT]
[FONT="] and impeller from the floor)."[/FONT]
If I wire according to the CW instructions above is this correct? Seems like the instructions are contradictory but maybe the orientation used by Leeson diagram on the box are the opposite from Clearvue?
Thanks for your help. Chuck
[FONT="][/FONT]
.
[FONT="]Use the CW wiring diagram from the motor plate.[/FONT]
[FONT="]a. L1 connects to P1[/FONT]
[FONT="]b. L2 connects to (T4 & T8)[/FONT]
[FONT="]c. P3 & T1 & T5 –wire together[/FONT]
[FONT="]d. The ground wire (bare wire) goes to a green screw inside the motor connection box[/FONT]
[FONT="]Then in the Note at bottom of Page 23 it states:[/FONT][FONT="]a. L1 connects to P1[/FONT]
[FONT="]b. L2 connects to (T4 & T8)[/FONT]
[FONT="]c. P3 & T1 & T5 –wire together[/FONT]
[FONT="]d. The ground wire (bare wire) goes to a green screw inside the motor connection box[/FONT]
[FONT="][/FONT]
[FONT="] [/FONT]
[FONT="] "Once the motor is wired, the motor shaft and [/FONT]
[FONT="] impeller blade should be turning counter-clockwise [/FONT]
[FONT="] when viewing from below. (ie: looking up at the motor [/FONT]
[FONT="] and impeller from the floor)."[/FONT]
If I wire according to the CW instructions above is this correct? Seems like the instructions are contradictory but maybe the orientation used by Leeson diagram on the box are the opposite from Clearvue?
Thanks for your help. Chuck
[FONT="][/FONT]